bikeindy
Senior Member
- Location
- Indianapolis IN
If you had no specs on a cabinet mount oven rated at 30 A what size conductor would you use?
Isn't "rated at 30 A" a spec?bikeindy said:If you had no specs on a cabinet mount oven rated at 30 A what size conductor would you use?
LarryFine said:Isn't "rated at 30 A" a spec?
M. D. said:#10 IBC. on a 30amp breaker
Depends on the appliance: is there a white wire?bikeindy said:would you run 10-2 w/g or 10-3 w/g?
LarryFine said:Depends on the appliance: is there a white wire?
Is this "guy at the appliance store" is qualified to give this advice? I once ran into a situation where the "guy at Big Orange" said that an electric dryer circuit needed 6-3 and a 50A receptacle and breaker. He was sure he was right and even defensively mentioned that he "went to school for electrical."bikeindy said:See here is my problem I will be running 8-3 wg ground because the guy at the appliance store said that is what is "required"
bikeindy said:But he said it was a 30A oven and above that will sit a 30 A microwave which they say also "requires a 8-3 w/g. I just would like to know what you all think about that.