What is the wiring method used?

What is the calculated load of the sub-panel?

The EGC is sized on Table 250.122 based on the overcurrent protective device.

Chris
 
Answer could vary depending on conditions (ambient, # of current carrying,termination tempt ratings, and most importantly, wiring method (NM is 60 degree) etc_) but basic answer is 310.16, #3 Cu is 100 amp, and 250.166 OCP not exceeding 100 = #8 (unless Romex)
 