lots of "depends" :)
25 kw @ 208 3 phase evenly distributed would be 69.4 amps

422.10 would require an ampacity of 86.8 amps in most cases

From there, it's a case of type wire, etc. #3 THHN normal conditions, yes
#3 NM, no #3 SE Interior wiring '05 Code yes '08 Code no
 
I do not know what that means. All I have is the information I stated, 25kw
at 69.39A. Says #3 wire is needed and would like to know how they came up with the wire size. What size breaker would you use?
 
What type of equipment are we dealing with ? (air handler with unit heat, duct heater, heat pump, package air unit, water heater)
 