augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Feb 26, 2010 #2 lots of "depends" 25 kw @ 208 3 phase evenly distributed would be 69.4 amps 422.10 would require an ampacity of 86.8 amps in most cases From there, it's a case of type wire, etc. #3 THHN normal conditions, yes #3 NM, no #3 SE Interior wiring '05 Code yes '08 Code no
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Feb 26, 2010 #3 Does the unit specify an MCA?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Feb 26, 2010 #5 25,000 / 208*1.732 for 3 phase 208
D Duffin Member Feb 26, 2010 #6 I do not know what that means. All I have is the information I stated, 25kw at 69.39A. Says #3 wire is needed and would like to know how they came up with the wire size. What size breaker would you use?
480sparky Senior Member Location Iowegia Feb 26, 2010 #8 Duffin said: Mca? What is that? Click to expand... Minimum circuit ampacity.
D Duffin Member Feb 26, 2010 #9 All the information I have I stated. Can you show me code # for my boss?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Feb 26, 2010 #10 You never stated the voltage.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Feb 26, 2010 #11 What type of equipment are we dealing with ? (air handler with unit heat, duct heater, heat pump, package air unit, water heater)