etinkham
Member
- Location
- DC, MD , VA
We have contractors currently installing a UPS. The wire size for the primary input of the UPS is 3 #2/0 + 1 #6 ground in 2" rigid conduit (per drawing). The wire type is XHHW-2. When the UPS arrived it had a 200-amp circuit breaker instead of 175-amp. Do we need to upgrade the wire size to 3/0? The terminations in the UPS are NOT labeled and listed for 90 degrees, therefore I believe the 75 degree C rating on Table 310-16 must be used.