Im on a project right now where carrier sent us the wrong air handlers (should've been 208v and the sent 460 volt) and our company's solution is to install a step up transformer. The A/H is only 15A and my foreman had us wire them in 12 AWG in and out. When I looked up the calculations and sized it myself it looks like we should be running minimum 6 AWG.
Since this was an unexpected scenario we're just submitting an as built for engineering. Can anybody shed some light on this and let me know if we're going to haVe to change the wire size?
For additional information they purchased 15kva step up transformers and the wire lengths are less than 10ft.