Wire Sizing- NEC VS Manufacturer Spec Sheets

Status
Not open for further replies.

Davinjw

New User
Location
Longivew, WA
I'm looking for High Flex cable good for Cable Trays and able to carry 400A. (800A Paralleled)

According to NEC, using the 75*C Column I need 500KCM to carry 400A.

according to the quote I got back with the following spec sheet, my cable is good for 704 Amps, and a 262KCM would carry my 400A load.

Trying to figure out if a Spec Sheet for a UL'ed product supersedes the NEC.

Thanks!

http://distributorwire.com/specs/2kvdlo.html
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
I'm looking for High Flex cable good for Cable Trays and able to carry 400A. (800A Paralleled)

According to NEC, using the 75*C Column I need 500KCM to carry 400A.

according to the quote I got back with the following spec sheet, my cable is good for 704 Amps, and a 262KCM would carry my 400A load.

Trying to figure out if a Spec Sheet for a UL'ed product supersedes the NEC.

Thanks!

http://distributorwire.com/specs/2kvdlo.html
Their rating is for 90deg C as "Locomotive" cable, you cannot use that rating. So you must use it based on the RH/RHW rating in the NEC table for 75C, which by the way says 500kCMIL is 380A for 3 conductors, but if you parallel, you have to de-rate to 80% for 6 conductors. So for 800A you will need 2 x 900kCMIL, or if you want to use that 262 DLO, you would need 4/phase.

Using DLO is not as straightforward as the vendors want you to think. You also MUST use approved lugs for Type K stranding or better, and very few mechanical lugs are approved for that. So you then usually end up having to use approved compression lugs and the special dies for them.
 

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)
Their rating is for 90deg C as "Locomotive" cable, you cannot use that rating. So you must use it based on the RH/RHW rating in the NEC table for 75C, which by the way says 500kCMIL is 380A for 3 conductors, but if you parallel, you have to de-rate to 80% for 6 conductors. So for 800A you will need 2 x 900kCMIL, or if you want to use that 262 DLO, you would need 4/phase. ....

Just asking: The OP said "cable tray". Does one need to derate to 80%?

ice
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
In general all of the manufacturer's ampacities for the "DLO" type cables are based on 90°C and the cable being in free air. It is not too often that you can use those ampacities for an NEC application.
 