What size wire would you use to get 100A from a USE-2 using table reference B.310.15(B)(2)(1).
1. If for 1 or 2 family 100% of load,
2. If for feeder wire to a sub panel.
My understanding is for #1 above I can size to 83% of the 100A that would give me a 2AWG in Al and 4AWG in Cu. But if it is a feeder for a sub panel as in #2 above I'd have to use a 1AWG in Al or 3AWG in Cu.
Is my understanding correct?
1. If for 1 or 2 family 100% of load,
2. If for feeder wire to a sub panel.
My understanding is for #1 above I can size to 83% of the 100A that would give me a 2AWG in Al and 4AWG in Cu. But if it is a feeder for a sub panel as in #2 above I'd have to use a 1AWG in Al or 3AWG in Cu.
Is my understanding correct?