wire sizing

Status
Not open for further replies.
In the last supervisor class that I took the instructor said that any branch circuit less than 100 amps must use the 60 degree column for wire sizing? This does not sound right as we all know that a #10 thhn is good for 35 amps in conduit & 30 amps in nmb romex. #8 good for 50 amps in conduit & 40 amps in nmb romex. Does anybody understand maybe what she was referring to? I have never heard of anything changing at the 100 amp mark.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
In the last supervisor class that I took the instructor said that any branch circuit less than 100 amps must use the 60 degree column for wire sizing? This does not sound right as we all know that a #10 thhn is good for 35 amps in conduit & 30 amps in nmb romex. #8 good for 50 amps in conduit & 40 amps in nmb romex. Does anybody understand maybe what she was referring to? I have never heard of anything changing at the 100 amp mark.

#10 copper of any insulation type is not allowed to have more than a 30 A OCPD on it. 240.4 (D).
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
#10 copper of any insulation type is not allowed to have more than a 30 A OCPD on it. 240.4 (D).


Not quite true but yeah in general

To the OP

The instructor is not totally correct. If all the equipment and termination are label and have a 75C rating then you can use the 75C for 100 amps and less. If the labeling is not there then you must assume 60C for those ampacities. Pretty safe to say you will not see any new stuff rated 60C as they are all rated at least 75C.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
1) In the last supervisor class that I took the instructor said that any branch circuit less than 100 amps must use the 60 degree column for wire sizing?

2)This does not sound right as we all know that a #10 thhn is good for 35 amps in conduit & 30 amps in nmb romex. #8 good for 50 amps in conduit & 40 amps in nmb romex.

3)Does anybody understand maybe what she was referring to? I have never heard of anything changing at the 100 amp mark.

1-They may be referring to the 60° C rating when 75° components are not used.

2-#10 THHN at 35 amps could only be used for specific loads as outlined on 240.4(G). As noted the rating for NM cable must be at the 60° C ampacity.
 