wire sizing
hienlam
here is a senerio,
i got an existing spare breaker(100A). i want to use this spare breaker and connect to a new unit equipment(x), which has a load of 70A. i connect this unit with a disconnect switch(100/70) 3poles. i want safe the cost of the wire...
is nec code allow me to size the wire base on 70A fuse???
charlie b
Lockport, IL
Semi-Retired Electrical Engineer
Re: wire sizing
Yes, unless this load will be running for more than 3 hours at a time. That would make the load ?continuous,? and you would have to size the conductors and the overcurrent protection device for 25% above the load. 125% of a 70 amp load is 87.5 amps, and that would bring you back to a 100 conductor and a 100 amp breaker.
david
Pennsylvania
Re: wire sizing
Hienlam
Are you saying you want to start with a 100-amp breaker and feed with a 70-amp conductor to a 100 amp fusible disconnect with 70 amp fuses?
don_resqcapt19
Illinois
retired electrician
Re: wire sizing
240.4 will require that you use 100 amp wire on the 100 amp breaker unless you can meet one of the tap rules in 240.21 or unless this is special application circuit such as a motor feeder.
Don
hienlam
Re: wire sizing
thanks for all the comments....you guys really heldful...again thanks
Davis...yes, that is what i meant...