Re: wire sizing
2-sets of 600kCmil is sufficent to supply 840A assuming two seperate raceawys. If all of the underground conductors are in the same raceway 310.15(B) (2) will apply for .
derating.
Know why are you delivering 840A capacity
there are numerous senarios that may work 4 sets of 3/0 200A per phase . This depends on the equipment and purchased lug configuration.
Does the feeder demand on the service require 800A ??
Charlie