wire sizing

Status
Not open for further replies.

dsbenevento

Member
Location
New York
i am running a feeder from a service panel to a 100a subpanel. 3phase. what size wire do i need to run and what size pvc rigid conduit do I need?

Darren
 
Re: wire sizing

Darren, you list yourself as an electrician, so in your code book a good start is article 310 and Annex C.

Roger
 
Re: wire sizing

You can use smaller conductors and conduit in most cases. Will the terminations in the main and subpanel be rated @ 75 deg? Will the neutral be considered a current carrying conductor (non-linear loads)? Any other derating to consider like temperature, etc?
 
Re: wire sizing

Originally posted by dsbenevento:
the terminations are rated 75deg yes There will be some nonlinear loads such as flourescent lights and heater fan motors.
You can use a number #3 or #2 depending on the type of load and voltage drop. Is the non-linear load over 50%?

Lady :)
 