i am running a feeder from a service panel to a 100a subpanel. 3phase. what size wire do i need to run and what size pvc rigid conduit do I need?
Darren
Darren
You can use a number #3 or #2 depending on the type of load and voltage drop. Is the non-linear load over 50%?Originally posted by dsbenevento:
the terminations are rated 75deg yes There will be some nonlinear loads such as flourescent lights and heater fan motors.
I guess the harmonics does not have to be factored into the equation. I would say a #2 to be safe, but that's JMO!Originally posted by dsbenevento:
the nonliear load is well under 50%.