hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
400A fused disco load side has 4#750 kcmil Al feeder.

Not sure if 750 kcmil Al is ok or should it be 800 kcmil Al?


Sent from my iPhone using Tapatalk
 

Carultch

Senior Member
Location
Massachusetts
400A fused disco load side has 4#750 kcmil Al feeder.

Not sure if 750 kcmil Al is ok or should it be 800 kcmil Al?

Sent from my iPhone using Tapatalk

I don't recall ever seeing a 400A disconnect that can accept 800 kcmil. What I've seen on 400A disconnects, is typically a "snowman lug" that can either accept 1 wire up to 750, or 2 wires up to 250 or 300. Either that, or a big and little side-by-side lug. You may be looking at paralleling if you need the full 400A of ampacity.

750 kcmil AL is of 375A for the 75C terminals which "rounds up" to "be protected by" 400A fuses per 240.4(B). You need to know the calculated load, and confirm it is less than 375A. In otherwords, the calculation that sizes the 400A fuses, prior to rounding up to the 400A standard size, needs to be less than 375A.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
As Carultch stated you can use the next size up rule in 240.4(B). What's the calculated load, is it greater than 385 amps? If not you can go up to the next standard size which is 400 amps.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
As Carultch stated you can use the next size up rule in 240.4(B). What's the calculated load, is it greater than 385 amps? If not you can go up to the next standard size which is 400 amps.

Calculated demand load is less than 385A right now. However, we are talking about feeder even if at some point load is greater than 385A next round up rule would make 750kcmil size would be ok no? Otherwise what point of having next round up rule it does not state calculated load has to be less than 385A?
 

Carultch

Senior Member
Location
Massachusetts
Calculated demand load is less than 385A right now. However, we are talking about feeder even if at some point load is greater than 385A next round up rule would make 750kcmil size would be ok no? Otherwise what point of having next round up rule it does not state calculated load has to be less than 385A?

The 750 kcmil AL wire is OK as long as the calculation that "rounds up" to 400A, is 385A or less, and it is a circuit where 240.4(B) applies. If the scope of the loads served by this disconnect increases beyond "adding up" to 385A, the 750 kcmil AL is no longer compliant. If it "adds up" to 395A, you'd need 800 kcmil AL, but verify that you can connect it first. If it "adds up" to 396A, you'd need the full 400A worth of wire, i.e. 2x 250 kcmil AL in parallel. If it is my choice in this example, I would parallel anyway, because it is less total kcmil of metal, and because smaller wires are more flexible.

I put "adding up" in quotations, because it isn't necessarily a direct addition of each device's full load amperes. Some loads do have their operating currents simply add, but loads in general do not. There are load diversity factors based on the reality that not every device is turned on simultaneously. There are also continuous load factors that may apply, depending on the details of how long the loads are expected to operate continuously. A safety factor applied so thermal-based OCPD's don't nuisance trip.

I do not understand the physical basis for why the next-size-up rule even exists in the first place. It would seem that the OCPD should be the weak link, such that it trips before the wire exceeds its ampacity. Especially when the calculated load isn't a fixed sum of current-limited devices, but rather a weighted sum that could be exceeded in a rare situation of high demand user behavior. But it is in the NEC, and we get to take credit for it when convenient for us.
 
Last edited: