Wire sizing
Redeagle91
Carrollton
Superintendent
I was on a jobsite and I came across this junction box with a terminal block in it. There are 3-480v 15 amp Blower coil units that are being fed from a 480v 50 amp breaker with #8 wire . It comes to this box and changes wire size to 3 sets of #12. Leaves there and goes to 3 separate 30 amp fused disconnects with 15 amp fuses in them. Should the wire from the terminal block to the disconnects be rated for 50 amps
How long are the conductors between the terminal box and the 15 amp OCPD?
25' would be the maximum length if applying the 25' tap rule.
The 25' tap rule requires an ampacity of at least 1/3 of the upstream OCPD, and for 50A, that would be 16.7A. So 75C rated #14 would comply, and #12 is only required if 60C rated or 60C limited (like NM per 334.80)?
Cheers, Wayne
Cheers, Wayne
Correct. The existing conductors are already #12 so they would be adequate for the 1/3 minimum ampacity of the 50 amp OCPD.
See 430.28(2)
Good point, the OP is about motor circuits, so 430.28(2) applies rather than the more general 240.21(B)(2). (*)
Still, I think the phrase "25' tap rule" is commonly understood to mean 240.21(B)(2), so my statement was correct, if off point relative to the OP. But the motor/non-motor aspect of the OP was not relevant for the point I was asking about.
Cheers, Wayne
(*) Does 430.28(2) mean that if I have grossly upsized my feeder conductors due to voltage drop, I am required to use a larger tap conductor than I would under 240.21(B)(2)? Or is it merely an additional allowance to what 240.21(B)(2) allows? Seems rather pointless to require a short section of "normal" sized feeder conductors between the upsized feeder conductors and the tap.
I'm thinking that the single feeder OCPD for a bunch of motors could be larger than the feeder conductor size so the actual size of the feeder conductor is used for the 1/3 rule.
Yes, that's the usual case, and so the reason for 430.28(2), which is more lenient than 240.21(B)(2). My starred question was about the unusual case where the motor feeder ampacity actually exceeds the OCPD rating because the feeder was upsized for voltage drop. Does 430.28(2) then become a penalty? One that could be sidestepped by having a short length of minimum ampacity feeder between the upsized portion and the tap, but that seems an unnecessary hoop to jump through.
Cheers, Wayne