Re: Wire Sizing
The service entrance conductors must always be sized equal to or exceeding the calculated or actual load, whichever is higher. That being said, another approach would be:
If this was a 1200A MLO main panel instead of a 1200A MCB main panel, then the 3X500's might be OK if they equal or exceed the calculated or actual load.
If you had a 1200A MLO main panel, you could have up to six (6) circuit breakers in it to serve various distribution or branch panels or other loads.
The trip size of the 6 CB's could add up to more than 1200A total, as long as each of the feeder circuit conductors & CB's were properly sized together.
In other words, you could have a 1200A MLO main panel with (for example) 4 each 200A feeders and 2 each 400A feeders. This arrangement is OK as long as each of the feeders are adequately sized and the total load on the main panel doesn't exceed the ampacity of the service entrance conductors. In essence, some of the 6 feeders are sized heavier than their load actually requires.
While this arrangement is code compliant, it places more burden on the EC's that work on the installation later. They must be certain that they don't inadvertently overload the service entrance. The safer (more idiot proof) way is to have a MCB that is sized to match the service entrance conductors -- that would prevent an inadvertent overload in the future. It's pretty easy for stuff to be added later such that the actual load exceeds the original calculated load.
But the MLO main panel with the 6-circuit rule is pretty common.
Edited to correct my lousy wording and spelling.
[ July 11, 2005, 01:23 PM: Message edited by: tx2step ]