ken44
Senior Member
- Location
- Austin, TX
I have 4 each of 400 Amp CB's that are located in a UPS, there are 2 CB's at each end of the UPS; I will be sizing the wire for these CB's from the 75 degree column of 310-16 per the terminal temperature rating of the CB's, Do I have to use 600 KCMIL (420 Amps@75 degrees)or does the NEC allow me to use 500 KCMIL (380 Amps@75 degrees) per the "next size up" rule?