I have 4 each of 400 Amp CB's that are located in a UPS, there are 2 CB's at each end of the UPS; I will be sizing the wire for these CB's from the 75 degree column of 310-16 per the terminal temperature rating of the CB's, Do I have to use 600 KCMIL (420 Amps@75 degrees)or does the NEC allow me to use 500 KCMIL (380 Amps@75 degrees) per the "next size up" rule?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
You can use 500 Kcmil conductors and the next size up rule provided that the calculated load on the feeder does not exceed 380 amps.