Wire Submittal Ampacities - Does 240.4(D) typically override Table 310.15? See example

Status
Not open for further replies.

CelectricB

Member
Location
Texas Panhandle
Occupation
MEP Designer
Here is a Southwire submittal sheet.

1674068488559.png
Is it safe to assume the small conductor ampacities are adjusted to 240.4(D)? Is this typical on wire submittals?
 

kwired

Electron manager
Location
NE Nebraska
see the footnote referenced with the + sign.

That table is factoring in 240.4(D) in its values which is for general use.

Now take a look at all the items mentioned in T240.3 that refer you to other articles for overcurrent protection. Many those cases you can use the ampacity mentioned in 310.16 (310.15(B)(16)) and forget about 240.4(D).
 

kwired

Electron manager
Location
NE Nebraska
It seems the table is not considering 240.4(D). Also note it does not specify copper.
Actually it says in the footnotes that 240.4(D) is applied to the values in the table.

The table is useless for when ampacity adjustments can apply or for situations when 240.4(D) does not apply.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
To the original poster, I would not concern myself with the chart from southwire for ampacities. The nec is what you need

Here is the note at the bottom of southwire table


1674138303650.png
 