Hello..
300.22 C exception mentions that for plenum "other area" a non plenum rated cable (NM) can pass thru perpendicularly.
When I look at LV wiring in 800.154(a) it mentions "in other spaces used for environmental air" as described in 300.22C
I'm assuming that if the LV wiring if not plenum rated like CM or CMX … it would still fall into the 300.22C exception…… and would not need to be plenum rated.,
But after reading thru 725.154(A)………. I then noticed that 800.154(a) actually says "described"
Looking into 725.154 (A) for CL2 and CL3 wire and see that It mentions the other spaces as "described" in 300.22C and goes on to say Only Type CL2P or CL3P cable shall be permitted to be installed in these raceways.
Are they calling the other space a raceway??
Am I to read it that non plenum CM or CL can't go though this other area as NM can, or does the exception of 300.22C also apply to these LV cables?
Thank you.
300.22 C exception mentions that for plenum "other area" a non plenum rated cable (NM) can pass thru perpendicularly.
When I look at LV wiring in 800.154(a) it mentions "in other spaces used for environmental air" as described in 300.22C
I'm assuming that if the LV wiring if not plenum rated like CM or CMX … it would still fall into the 300.22C exception…… and would not need to be plenum rated.,
But after reading thru 725.154(A)………. I then noticed that 800.154(a) actually says "described"
Looking into 725.154 (A) for CL2 and CL3 wire and see that It mentions the other spaces as "described" in 300.22C and goes on to say Only Type CL2P or CL3P cable shall be permitted to be installed in these raceways.
Are they calling the other space a raceway??
Am I to read it that non plenum CM or CL can't go though this other area as NM can, or does the exception of 300.22C also apply to these LV cables?
Thank you.