Wire Trough connections

Status
Not open for further replies.

mtnelectrical

Senior Member
when you guys do some services.do you use split bolts or those multi tap connectors (ilsco or blackburn or similar) when you make the connections inside the trough? I will do a Upgrade and I wonder which way it has worked better for you guys. I am using a wire trough 6"x6"x48" then 3- 100 amps meter pans (that's how we call it here in Jersey) and then run to the basement.To use split bolt there would be a 2/0 copper and 3 - #4 per connection,the web site below just shows one connector for 3 connections we will need for 4 connections.Three would be needed (L1,L2 and Ground)


http://www.drillspot.com/products/44..._Tap_Connector
 

JES2727

Senior Member
Location
NJ
Split bolts are cumbersome and time consuming. Use the polaris/ilsco/burndy type tap. You'll be glad you did. They are available with four holes.
 

mtnelectrical

Senior Member
I see. Looks like it is a time saving thing. I just got 3 for my next service, they are not cheap $27.72 each 4/0 4 ports, but when you guys used split bolts are they listed to connect more than 3 wires together?
 