Some people think it’s redundant to do, others don’t like the idea of a mechanical connection of conduit being their low impedance fault current path to clear a fault.
As well as certain companies and specs a lot of times in my areas of work always require a wire type EGC.
It is a myth that common electrical hardware (metallic conduits, cable trays when properly installed AS an EGC) are inferior to copper cable. Quite the opposite is true. Certain Codes (hospitals) require redundant grounds and an EGC certainly fulfills that role. There are also differences in performance in terms of surge and higher frequencies so a stranded ground conductor is often recommended for lightning protection systems and variable frequency drives.
It is also a myth that grounding is always the solution. The idea is two fold. The first is that it keeps people who are normally grounded close to the same potential as the surfaces of electrical equipment. As distances increase or if ground loops are present such as with bracket grounding or multiple system bonding jumpers this condition may no longer hold. NEC mandates single point grounding and OSHA requires work site (single point) grounding.
The second idea is that given a low enough impedance short circuit protection can do double duty for both phase to phase and phase to ground faults. Again impedance causes major issues on larger systems. For instance say a circuit breaker on a 208 V system uses a 100 A breaker. The short circuit trip will be 1000 A using typical UL 489 B curves. The phase to ground voltage is 120 V so if the impedance exceeds 0.12 ohms, it won’t trip properly. This condition is easily achieved with very short distances.
As cable lengths increase grounding via cables or equipment is no longer effective. However as the following report shows steel conduit and EMT is vastly superior to EGCs.
Download the free GEMI Analysis Software to:– confirm wire-type equipment grounding conductors provide an effective ground-fault current path– confirm steel...
steeltubeinstitute.org
Multi grounded systems become a necessity as Earth has a 2D grounding system actually decreases impedance with distance (see IEEE Green book). Summary: resistance grows linearly with distance but the number of paths grows with the square of distance. So the net result is resistance is proportional to the inverse of the distance. Alternatively we can use common mode detection and tripping (sum of the phase currents should equal zero, the GFCI operating principle) or at extreme distances using distance relays which trip if the measured impedance falls under a certain range.
So if you are working residential this is mostly a lot of detail you never need to know. In a utility environment it’s baked into the design. In commercial and industrial it’s very easy to cross over from effective grounding to ineffective grounding. If anything the GEMI software and some tables produced with it are good at keeping you between the ditches.