Wire Type for Burial?
Hello,
I'm an engineer but this is beyond my practice. Here's the deal: building a new small shop about 70' away from the pole with meter and disconnect. Got the wire size figured out just fine, 4/0-4/0-4/0-2/0 AL. The wire has to be buried. Question is, what type of wire and should it (or not) go in a conduit?
Just not anything I've had to deal with before. Thanks.
I had temporarily closed this thread, in order to determine whether this was a DIY project. The OP convinced me, in a PM, that it is not, that it relates to his business. I am therefore reopening the thread. I offer my apologies to the OP for the delay and the inconvenience.
Hello,
If you want to direct bury it, then URD is the way to go. I wouldn't do it that way unless the soil is sandy with no rocks to cause you grief later. If you run conduit, I'd go with 2 1/2" PVC and use XHHW conductors.
If I may, use care :), "URD" (with only that rating) is actually a utility conductor and not recognized by the NEC. USE or UF would be a recognized conductor for direct burial (some 'URD' has added ratings).
For installation in a raceway, most any conductor with a "W" in the insulation. I agree the most common would probably be XHHW.
We do not direct bury unless the customer fully understands he is responsible for all rodent damage. Not even a tail light warranty. Usually the first repair would have paid for conduit, not counting the down time and PIA factor.
Rocks are not near the problem here.
Agreed........In my area, the URD most supply houses carry is the 8000 version which is RHH/RHW2 which is legal to install inside as well as outside a structure.
From personal experience you should be just as concerned with rodent damage when using conduit unless you've sealed both ends.
We do not direct bury unlesin the customer fully understands he is responsible for all rodent damage. Not even a tail light warranty. Usually the first repair would have paid for conduit, not counting the down time and PIA factor.
We do duct seal, but once the box is on and covers closed, it is up to the owner to keep them on.
I learned early on just how much damage a mouse can do to a brand new pump panel in one night.:rant:
That is the owners problem if they can't leave covers on. If rodents get into the underground raceway at least you can (usually) pull conductors out without digging everything up.