As its name implies, an auxiliary gutter provides additional gutter space for wiring in various types of electrical enclosures and equipment. This additional gutter space may be necessary to provide sufficient room for the number of conductors in an enclosure or to provide adequate wiring bending/deflection space where conductors connect to a terminal. Although the construction of an auxiliary gutter is no different from that of a wireway, it is the field application of this equipment that differentiates an auxiliary gutter from a wireway.
A wireway is a raceway in accordance with the definition of raceway in Article 100. Auxiliary gutters supplement enclosure wiring spaces and are not encompassed by the definition of raceway. Therefore, Code requirements that apply only to raceways do not apply to auxiliary gutters. An example of such a requirement is 230.7, which prohibits service conductors from being installed in a raceway with conductors that are not service conductors. This rule applies to wireways installed in accordance with Article 376 and 378. However, an auxiliary gutter installed to supplement the wiring space of a service equipment enclosure is not a wireway and therefore is not subject to 230.7.
2011 Handbook
An auxiliary gutter provides additional gutter space for wiring in various types of electrical enclosures and equipment. This additional gutter space may be necessary to provide sufficient room for the number of conductors in an enclosure or to provide adequate wiring bending/deflection space where conductors connect to a terminal. Although the construction of an auxiliary gutter is no different from that of a wireway, the field application of this equipment differentiates an auxiliary gutter from a wireway.
A wireway is a raceway in accordance with the definition of raceway in Article 100. Auxiliary gutters supplement enclosure wiring spaces and are not encompassed by the definition of raceway. Therefore, Code requirements that apply only to raceways do not apply to auxiliary gutters. An example of such a requirement is 230.7, which prohibits service conductors from being installed in a raceway with conductors that are not service conductors. This rule applies to wireways installed in accordance with Article 376 and 378. However, an auxiliary gutter installed to supplement the wiring space of a service equipment enclosure is not a wireway and, therefore, is not subject to 230.7.
2014 Handbook