As hard as it is to believe, there is some controversy as to the 6X, 8X rule.
I've seen two schools of thought here. One is based on the wording "the distance between raceway and cable entries enclosing the same conductor " with proponents stating that, unlike a pull box, the distance from the conduit entry to the opposite wall was not determined by the 6X, 8X rule only the distance between raceways..
Thats the way I have always looked at it.I know of inspectors, and I have substantiation of the thinking from a CMP, that the 6X,8X applies to opposite walls just as it would with a pull box.