1 1/2" EMT how many # 12 THHN WIRE CAN BE PULLED? 2002 code
S serg_at_allmarc New member Location Illinois Apr 14, 2003 #1 1 1/2" EMT how many # 12 THHN WIRE CAN BE PULLED? 2002 code
T txsparky Member Location Conroe, Texas Apr 15, 2003 #2 Re: Wirefill quick question ANNEX C Table C2 says 58
C charlie tuna Senior Member Location Florida Apr 15, 2003 #3 Re: Wirefill quick question surg-------what would the "deration" for #12 be with 58 wires!!!!!!!!!!!!!!!!!
Re: Wirefill quick question surg-------what would the "deration" for #12 be with 58 wires!!!!!!!!!!!!!!!!!
charlie b Moderator Staff member Location Lockport, IL Occupation Semi-Retired Electrical Engineer Apr 15, 2003 #4 Re: Wirefill quick question Derate to 35% of 30 amps, or 10.5 amps. My group was discussing this topic yesterday. The circuits of interest drew only 1-2 amps each, so the de-rating did not matter.
Re: Wirefill quick question Derate to 35% of 30 amps, or 10.5 amps. My group was discussing this topic yesterday. The circuits of interest drew only 1-2 amps each, so the de-rating did not matter.
S sparkmantoo Member Location Virginia Apr 17, 2003 #5 Re: Wirefill quick question table 310-15 are based on no diversity. loaded to their maximum rated load. for load diversity you should see table B310-11 in appendix B.
Re: Wirefill quick question table 310-15 are based on no diversity. loaded to their maximum rated load. for load diversity you should see table B310-11 in appendix B.
S sparkmantoo Member Location Virginia Apr 17, 2003 #6 Re: Wirefill quick question excuse me i mean table 310-15(b)(2)(a). sorry for being a d.a. :roll: