Hi All,
I hope everyone had a good day. Does article 386 indicate you can’t use a wiremold box, with a light mounted on it, in an open porch? That is How I interpret it. I have seen it done many times but I have always said it’s wrong. 386.2 defines the box as part of the raceway and it’s not listed for damp location in 386.10. The application is extending the switch leg for the porch light to the outside porch ceiling. It’s a brick wall. Out of all people, the supply house told my customer that I am wrong. Any opinions?
Jim
ARTICLE 386 Surface Metal Raceways
I. General
386.1 Scope. This article covers the use, installation, and construction specifications for surface metal raceways and associated fittings.
386.2 Definition.
Surface Metal Raceway. A metallic raceway that is intended to be mounted to the surface of a structure, with associated couplings, connectors, boxes, and fittings for the installation of electrical conductors.
386.6 Listing Requirements. Surface metal raceway and associated fittings shall be listed.
II. Installation
386.10 Uses Permitted. The use of surface metal raceways shall be permitted in the following
1)
In dry locations.
(2)
In Class I, Division 2 hazardous (classified) locations as permitted in 501.10(B)(3).
(3)
Under raised floors, as permitted in 645.5(E)(2).
(4)
Extension through walls and floors. Surface metal raceway shall be permitted to pass transversely through dry walls, dry partitions, and dry floors if the length passing through is unbroken. Access to the conductors shall be maintained on both sides of the wall, partition, or floor.
Here is the electrical code definition of damp location:
Location, Damp. Locations protected from weather and not subject to saturation with water or other liquids but subject to moderate degrees of moisture. Informational Note: Examples of such locations include partially protected locations under canopies, marquees, roofed open porches, and like locations, and interior locations subject to moderate degrees of moisture, such as some basements, some barns, and some cold-storage warehouses.
Jim
I. General
386.2 Definition.
II. Installation
In dry locations.
(2)
(3)
(4)