lingwai1

Member
Location
Illinois
I had a quick question, that i was hoping someone out there would know! i recently got a violation on a job, where i had used wiremold in a sunroom extension on a house. My violation was because i did not use the correct amount of strapping divices to support the wiremold...My question is, what is the offical code # and quote, about strapping requirments on horizontal wiremold raceways???? Thank you SOO much guys
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: WIREMOLD CODE ILLINOIS

From the NEC he might just hit you with 300.11 (A) Raceways, cable assemblies, boxes, cabinets, and fittings shall be securely fastened in place.

Did you support it according to the manufactures instructions?

[ July 08, 2003, 09:30 PM: Message edited by: iwire ]
 

russ

Senior Member
Location
Burbank IL
Re: WIREMOLD CODE ILLINOIS

I agree Bob, There doesn't seem to be anything more definite than that.

lingwail, are there any installation instructions you could say you followed.

Russ