wireday
Senior Member
- Location
- New England
- Occupation
- Master electrician
Are wire nuts allowed inside control boxes of portable equipment, If not is there a suitable alternative like wago connectors ?
Splices (NFPA 79, Sec. 16.1.4). You are required to run conductors and cables from terminal to terminal without splices. However, an exception allows you to install a splice in leads attached to electrical equipment, such as motors and solenoids,
This is why I am asking about wire nuts, I wanted to come into junction box with power and divide it up into 4 wires using wire nut for components of junction box. This NFPA79 makes it sound like I should daisy chain from terminal to terminal.
Because they are inferior or because you don't ordinarily see them on something manufactured?But if I bought a machine from you and when I opened it up I saw a bunch of wire nuts, that would be the last one I would buy from you.
The only time I would use a wire nut on a piece of machinery is if I was out in the field with no parts making a "bush fix". So when I see them, I think of that and assume someone has bush fixed it. The exception would be an end device, like a solenoid valve or small cooling fan motor, where the manufacturer used flying leads and there is a small j-box for making the connections so there is no room for a TB.Because they are inferior or because you don't ordinarily see them on something manufactured?
Any termination is only as good as how well the installer followed instructions. Sure a wire nut may have higher probability to fail, but a properly installed wire nut likely has less chance of failure than something not properly installed.
I'll admit if I see wire nuts in something that was factory assembled - it is usually a sign someone has modified something though.