Wires must be protected, in 7' perimeter???

bwilliams627

Member
Location
Orange Beach Al.
Occupation
Electrician
This is one of the notes left by the inspector after his rough-in inspection on a new construction project that we are finishing up. The inspector is applying this to the attic access ladder. I've never heard of this rule. Has anyone else?
 

Eddie702

Licensed Electrician
Location
Western Massachusetts
Occupation
Electrician
If the attic has a permeant stairway like a pull-down stairway or walk upstairs the wiring needs to be protected within x# of fee from the attic entrance (6' I think).

If it a scuttle hole where you use a step ladder it does not need protection. At least that was my understanding.
 