wires on breaker
katriz1111
New member
how many branch circuit wires can be terminated on 1 breaker and where do i find it in the nec?
[ July 13, 2003, 09:21 PM: Message edited by: katriz1111 ]
websparky
Cleveland, Ohio
Re: wires on breaker
Here is a code reference for your answer.
The device also needs to be "listed" for the purpose.
NEC 2002 110.14 Electrical Connections.
(A) Terminals.
Terminals for more than one conductor and terminals used to connect aluminum shall be so identified.
Hope this helps,
Dave
[ July 13, 2003, 09:26 PM: Message edited by: websparky ]
tom baker
Bremerton, Washington
Master Electrician
Also 110.3(B) equipment shall be installed and used according to its listing instructions. Look at the CB, on the side or end it will tell you the size, number and torque for allowed conductors.
Most CB's allow two conductors per terminal for the smaller sizes CB's. You can always come off the CB and then use a splice several other conductors. There is a limit on the number of splices and conductors, but its 75% and 40%, which is hard to exceed.