I have 28 apt feeders from 3ph 120/208 service that have to get to 7 4- stacked meter modules (everything is in basement) and no wall above them so will need a wireway. It's crazy to think an inspector or anybody would allow all those conductors (84) to go in one wireway without a crippling ampacity adjustment? Art 376 no adjustment up to 30 conductors.
My question is would you use just the # of conductors over 30 to determine which line in 310.15(c)(1) or once you're over 30 the ampacity reduction would start at 45%?
30 conductors no adjustment
34 conductors 40% or 80%?
Luckily Massachusetts amends 310 table if diversity is likely.
Opinions?
My question is would you use just the # of conductors over 30 to determine which line in 310.15(c)(1) or once you're over 30 the ampacity reduction would start at 45%?
30 conductors no adjustment
34 conductors 40% or 80%?
Luckily Massachusetts amends 310 table if diversity is likely.
Opinions?