An electrical installation being inspected is using 10" x 10" x 60" long wireway. There is an 90 degree elbow at one end. The other end is open. The elbow connects to a generator mounted circuit breaker enclosure. The conductors are (5) 600kcmil per phase and neutral. (lots of copper)
Horizontal conductors pass out of the circuit breaker enclosure and into the wireway. Where the conductor begin their sweep into a vertical orientation the pass by the internal corner of the wireway. Unfortunately the wireway was not specified with a sweep elbow. I am concerned the conductor insulation may be stressed where it passes by the internal corner with possible future rub through to cause a ground fault.
So what code references can I count on to require separation of the conductor from the inside corner edge of the wireway?
I see NEC 314.28(B) but do not understand what "conductors shall be cabled or racked up in an approved manner" means.
Horizontal conductors pass out of the circuit breaker enclosure and into the wireway. Where the conductor begin their sweep into a vertical orientation the pass by the internal corner of the wireway. Unfortunately the wireway was not specified with a sweep elbow. I am concerned the conductor insulation may be stressed where it passes by the internal corner with possible future rub through to cause a ground fault.