Looks like there probably is more then 30 conductors at at least one cross sectional area.
What are the load currents though?
If 480 volts and all motors are no more then 5 HP - 14 AWG still has sufficient ampacity after adjustments. 12 AWG would be fine for no more then 10 HP motors.
I'm with Rob on this-this is harmless. How is this any different than a large cross section of conductors in a panelboard? So it is a violation in the wireway but not the panelboard. Or if this was a nipple 24" or less and crammed to 60% fill it would also get a pass. An insult to one's common sense.
Next we can argue if it is being used as wireway or pull box-another crazy area of the code.
it seems to be more of a pullbox than a wireway to me.