If I have a 10x10 inch wireway that I am entering from the back with (2) 3 inch rigid nipples, (opposite the removable cover) and exiting out the bottom with (2) 3 inch rigid nipples.
The wireway is mounted vertically. Does it need to be a minimum of 6x3 =18 +3+3+3=27 inches in length? With 18 inches between raceways containing the same conductors?
I know 312.6 (a) (1) and (A) (2) allows the depth to be less than 10 inches. But is 10 inches wide legit?
Sizing wireway and pull boxes is as confusing as trying to figure out what a class 1, class 2 or class 3 circuit is.
The wireway is mounted vertically. Does it need to be a minimum of 6x3 =18 +3+3+3=27 inches in length? With 18 inches between raceways containing the same conductors?
I know 312.6 (a) (1) and (A) (2) allows the depth to be less than 10 inches. But is 10 inches wide legit?