chrisplusian
Member
- Location
- Orange Park, FL
- Occupation
- Automation Systems Engineer
I have always supported wireway at ends and at five foot intervals. 376.30(A) says "wireways shall be supported where run horizontally at each end and at intervals not to exceed 1.5m (5ft) or for individual lengths longer than 1.5m (5ft) at each end or joint, unless listed for other support intervals. The distance between supports shall not exceed 3m (10ft).
I have notes from when I did my apprenticeship in the 2002 code cycle. The code read exactly the same. I drew a picture, in my notes, to show if it was a long run of wireway that you had to support ends and at 5' intervals and another picture to show a single section of wireway used which was over 5' but less than ten that it only had to be supported at the ends. My notes said "this is only allowed for single isolated sections". My question now, comes from working with an industrial customer who said if the wireway sections are 10' that they only have to be supported at the joints, because the code says "or for individual lengths longer than 1.5m (5ft) at each end or joint. They make a good point.... if when the code says "for individual lengths" they meant a single section of wireway then why would it include joints?
I am now confused about the requirement. I even bought the mike holt "understanding the code" book and looked in there. He did a sad explanation of the requirement. He addressed the simple part... the one I have always used. The part of the requirement that starts at "or" is hard to understand, and he did not address.
My question: What exactly does the second part of the requirement (or for individual lengths longer than 1.5m (5ft) at each end or joint, unless listed for other support intervals) mean?
I have notes from when I did my apprenticeship in the 2002 code cycle. The code read exactly the same. I drew a picture, in my notes, to show if it was a long run of wireway that you had to support ends and at 5' intervals and another picture to show a single section of wireway used which was over 5' but less than ten that it only had to be supported at the ends. My notes said "this is only allowed for single isolated sections". My question now, comes from working with an industrial customer who said if the wireway sections are 10' that they only have to be supported at the joints, because the code says "or for individual lengths longer than 1.5m (5ft) at each end or joint. They make a good point.... if when the code says "for individual lengths" they meant a single section of wireway then why would it include joints?
I am now confused about the requirement. I even bought the mike holt "understanding the code" book and looked in there. He did a sad explanation of the requirement. He addressed the simple part... the one I have always used. The part of the requirement that starts at "or" is hard to understand, and he did not address.
My question: What exactly does the second part of the requirement (or for individual lengths longer than 1.5m (5ft) at each end or joint, unless listed for other support intervals) mean?