Alright so here,s what I have. This has already been inspected and passed but my boss came in and pretty much trashed the whole thing and wants me to have my guys rework.
11 - 1 inch o cal emerging from slab on which I installed a 10x10x 5ft wireway.
On top of the wireway we have two lighting panels. 40 circuit 3 phase On the left 150 amp on the right 100 amp
Between both panels (That is between panel and trough) I have Three two inch galvanized nipples
Both panel feeds were brought down the left side of panels from overhead into trough and into the first nipples as the mains are on bottom and this kept feed conductors out of panel .
The debate is, My bosses contention is that I should have my spacing between conduits as he points between the one inch slabbed branch circuits on the bottom of wireway and the two inch feeder emts from above on the top of the wireway as if it were a pull or junction box. Ive been doing this a long time and theres just no arguing with him. Opinions??
11 - 1 inch o cal emerging from slab on which I installed a 10x10x 5ft wireway.
On top of the wireway we have two lighting panels. 40 circuit 3 phase On the left 150 amp on the right 100 amp
Between both panels (That is between panel and trough) I have Three two inch galvanized nipples
Both panel feeds were brought down the left side of panels from overhead into trough and into the first nipples as the mains are on bottom and this kept feed conductors out of panel .
The debate is, My bosses contention is that I should have my spacing between conduits as he points between the one inch slabbed branch circuits on the bottom of wireway and the two inch feeder emts from above on the top of the wireway as if it were a pull or junction box. Ive been doing this a long time and theres just no arguing with him. Opinions??