almost.... The 350 requires the distance to a removable cover to comply with 312.6(A) which list 350 at 5".
Using the wireway as an LB is fine but with the 350s your wireway would need to be a 6x6
References are correct... but it all starts under 376.23 (assuming it's a metal wireway).314.28(A)(2)exception sends me to 312.6(A), which states I need 5" as min. for 350 mcm, its a 4" trough so its a violation. Thats my thought, looking for confirmation