Wireway used as pull box, do I have to derate?

Status
Not open for further replies.

jusme123

Senior Member
Location
NY
Occupation
JW
If I use a wireway as a junction box, do I have to derate?

The scenario is a 6’ length of 12”x12” wireway, I am mounting on wall, coming into the far backside with 3- 2 1/2” conduits, than nippleing 3’ down on opposite side of wireway with the 3 conduits into panel
053821f8d1b67b857c74f73da40de229.jpg



Sent from my iPhone using Tapatalk
 
Wireway used as pull box, do I have to derate?

Yeah, just saw it 376.22(B)

Thank you.