Wireway with Sec

Status
Not open for further replies.

nickelec

Senior Member
Location
US
So I I'm currently installing a 1200A service switch to fee an Mdp with multiple breakers for a PV system

I'm using multiple 10x10 wire ways and fittings from the existing service switch to my new set up all wire way no conduit connectors lock nuts etc

My question is do I need to bond all these pieces together? or because their metalic and I'm using couplings and flanges all bolted together I should be good. See attached pics

659fc986ab5d91b92d2899a14b66f004.jpg
3cd2e1005b7f44b72a78e0d2e8b1f2a2.jpg


Sent from my SM-S906U using Tapatalk
 

nickelec

Senior Member
Location
US
I can't imagine those bolted joints not qualify for bonding.
I would agree was just double checking. Inside this wireway would be SECs three sets of 500 tapped to existing bus section of existing service switch.

Sent from my SM-S906U using Tapatalk
 