Greetings!
I've been reading over your forums and haven't found one with the info I'm looking for.
In article 376 it gives all the requirements specific to wireways except which chart to use for conductor ampacities. 376.22 tells us that derating for multiple conductors doesn't begin until you have more than 30 CCC's. But which chart would I derate from? We will be using 90C wire from a 2000KW generator to the switchgear via wireway. The rest of the equation I pretty much understand, it's the cable sizing to start with I'm a little hazy on.
Thank you for sharing your expertise.
I've been reading over your forums and haven't found one with the info I'm looking for.
In article 376 it gives all the requirements specific to wireways except which chart to use for conductor ampacities. 376.22 tells us that derating for multiple conductors doesn't begin until you have more than 30 CCC's. But which chart would I derate from? We will be using 90C wire from a 2000KW generator to the switchgear via wireway. The rest of the equation I pretty much understand, it's the cable sizing to start with I'm a little hazy on.