I was told by an engineer and I can not get my fingers around as it seems to be circular. I have a 3-2" conduits and 3- 1 1/2" conduits entering the back of a 8 x 8 x 48" wireway. I was told I have to use the pullbox code as it is used as a pullbox not a wireway, thus using the 6 times the size of the largest conduit which would ultimately be 12" plus the additional measurement of the additional conduits which would be a wireway of 18" minimum. Is this correct and also what determines if this is used as a pullbox or wireway.