I work for a company that doesn't believe in multi-conductor circuit so we pull a neutral with each hot on 120v and 277v circuits. Many times because it seems to take a while to get the panels in we mount wireways above the panels and bring our pipes into the wireways. In the past this has not been a problem but as of late it has been due to the enforcement of art. NEC? 376.22(8) which states, Wireway exceeding (30) current carrying conductors shall be subject to adjustment factors as defined in NEC Article 376.22(8).
From the wireway to the panel we use a couple of 2" conduits less than 24" in length. Where the wires enter the 2" you will in fact have more than 30 current carrying conductors in a 42 circuit load panel because you must count the neutral. Yet the code allows you to pack the 2" if less than 24" and the panel gutter has no restrictions for more than 30 current carrying conductors. So I'm wondering why do wireway have it?
I was told by the inspector that it was due to heat but that doesn't really make sense to me because the leakest part of any circuit is where you have terminations. Also if I used a couple of 10x10x6" j Boxes I believe this would be allowed because there is no 30 current carrying conductors rule for boxes.
I really just looking for some solid reasoning behind art 376.22(8). Your input would be helpful Thanks
From the wireway to the panel we use a couple of 2" conduits less than 24" in length. Where the wires enter the 2" you will in fact have more than 30 current carrying conductors in a 42 circuit load panel because you must count the neutral. Yet the code allows you to pack the 2" if less than 24" and the panel gutter has no restrictions for more than 30 current carrying conductors. So I'm wondering why do wireway have it?
I was told by the inspector that it was due to heat but that doesn't really make sense to me because the leakest part of any circuit is where you have terminations. Also if I used a couple of 10x10x6" j Boxes I believe this would be allowed because there is no 30 current carrying conductors rule for boxes.
I really just looking for some solid reasoning behind art 376.22(8). Your input would be helpful Thanks