Re: Wirin a spray boot for an auto shop
I'll correct your citation George.
NEC 2002 Section 516.4(A) refers back to Art 501. You identified the interior as Division 1 then cited the Zone wiring methods. You should have referred to 501.4(A). The two systems don't mix and match well unless you know exactly what you're doing; very people few do.
The 2005 NEC now recognizes Zone systems for spray applications.
In any case, there is no specific requirement for either stranded or solid conductors. In fact, if you read the FPN No. 2 to 501.5, you may draw the conclusion that solid is preferred. This is not true. IMO the FPN is almost pure bunk designed to sell compact conductors.