Wiring 0-10v
mstrlucky74
NJ
Need a little help with wiring here. So the type B&Cfixtures show as 4 wire 0-0v in the schedule. The cuts show input as 120v. Twoquestions:
1. Don’t think I need to bring 4 wires to the fixture
2. I don’t think I need 0-10v wiring from switches tofixture.
3. If I’m correct on #2 were is the 0-10v…within thefixtures? They do have 0-10v drivers.
Just want to make sure I wasn’t confusing it and it was theother way around and bringing 0-10v to fixture then the driver to light is120v. 99% it’s 120v wire from switch to driver. The 4 wire 0-10v listed in the schedulethrew me off. Thanks.
This link is for the switch for the type B.
https://www.lutron.com/TechnicalDocumentLibrary/369748.pdf
The fixture driver has the 0-10 integrated... The dimmer switch referenced will not work to dim the lights, you need one specifically for 0-10. If there is no controllers involved, ie. Nlight, stopper... Etc then you would need to run the four conductor wire (power and 0-10 control) from switch to lights
Sent from my SM-N950U1 using Tapatalk
That is the dimmer switch you need to use for 0-10 dimming application
If you need to dim the light they sell the mc with the 0-10v volt wire inside or you can use cat5 or cat6 long side the mc
Sent from my SM-N950U using Tapatalk
Yes I know, the MC PCS cable, thanks. Wondering if the make hospital grade...have to check.
Edit..they do.:D