Wiring 240v receptacles with a single 240v phase?

Status
Not open for further replies.

andykee

Member
Location
United States
If I have a 3 phase combiner panel with 240v on a single phase(435v ph-ph), can I feed each hot pin of a nema6 15 outlet from the same phase to get 240v?
 

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
Two conductors from the same phase gives you 0 volts.

How many conductors are there on a single phase?

He said he got 435 volts on a single phase. I took it that he was asking if putting a 240 volt receptacle on that phase was acceptable.

It looks like you took it as each conductor was a 'phase' and two parallel conductors were going to be run to the receptacle from a single conductor, which would indeed give 0 volts from conductor to conductor.

I think we may need some clarification from the OP, but I think the jist of it is that he can't get 240 volts without a transformer.
 

iwire

Moderator
Staff member
Location
Massachusetts
How many conductors are there on a single phase?

He said he got 435 volts on a single phase. I took it that he was asking if putting a 240 volt receptacle on that phase was acceptable.

It looks like you took it as each conductor was a 'phase' and two parallel conductors were going to be run to the receptacle from a single conductor, which would indeed give 0 volts from conductor to conductor.

I think we may need some clarification from the OP.

I think it is clear

can I feed each hot pin of a nema6 15 outlet from the same phase to get 240v?
 

andykee

Member
Location
United States
I was working through an enphase design guide and saw they had a nema 6 15r plug on a monitoring device (250v envoy-c) wired in to a 480v panel and was wondering how to wire it. (screenshot attached)
 

Attachments

  • Screen Shot 2016-04-22 at 10.55.03 AM.jpg
    Screen Shot 2016-04-22 at 10.55.03 AM.jpg
    19.7 KB · Views: 0

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
I think it is clear

Not so much as you think. What is the definition of a phase? To me, a phase IS two conductors. To others, it is a single conductor.

To me, the following would put 435 volts on the receptacle, as I consider a phase to be two conductors.

can I feed each hot pin of a nema6 15 outlet from the same phase to get 240v?

No matter, I think we agree that it won't work the way he wants it. If he thinks a phase is a single conductor, he will get 0. If he thinks a phase is two conductors, he would get 435.

If there was a neutral, he could get 250 volts from 435. That's pretty close to 240.
 

iwire

Moderator
Staff member
Location
Massachusetts
I was working through an enphase design guide and saw they had a nema 6 15r plug on a monitoring device (250v envoy-c) wired in to a 480v panel and was wondering how to wire it. (screenshot attached)

The screenshot indicates it is a wye so there is a neutral, you would use one ungrounded phase and the grounded conductor/ neutral to get 244 volts to the receptacle.
 

iwire

Moderator
Staff member
Location
Massachusetts
So if the system is 422Y/244 V can I wire that outlet as L1 and Neutral on each of the receptacle horizontal pins?

The only issue I see with that is a NEMA 6 outlet is marked for two ungrounded conductors and you will have an ungrounded and a grounded conductor.

It will work but I am not sure if it is a listing violation.
 

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
The only issue I see with that is a NEMA 6 outlet is marked for two ungrounded conductors and you will have an ungrounded and a grounded conductor.

It will work but I am not sure if it is a listing violation.

That was my concern, too. Using, instead, Nema 7-15 for 277 volts would only have one hot, as it would be one leg of a 480 volt three phase to neutral, meaning only one ungrounded connector.

But then, it's a 277 volt design fed with 240-250 volts.

90441.jpg
 

iwire

Moderator
Staff member
Location
Massachusetts
That was my concern, too. Using, instead, Nema 7-15 for 277 volts would only have one hot, as it would be one leg of a 480 volt three phase to neutral, meaning only one ungrounded connector.

But then, it's a 277 volt design fed with 240-250 volts.

90441.jpg

Nice find, I might be more inclined to use that one.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
If the panel has neutral L-N and call it a day. Make sure your breaker can handle 240 volts to ground, In North America this usually dictates a 277/480 volt rated panel.
 