Wiring after the seal fitting

Status
Not open for further replies.

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
That might comply with 300.12 (or might not), but in the case of a junction box, wouldn't it violate:

314.17 (A) Openings to Be Closed. Openings through which conductors enter shall be closed in an approved manner.

Cheers, Wayne
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
That might comply with 300.12 (or might not), but in the case of a junction box, wouldn't it violate:

314.17 (A) Openings to Be Closed. Openings through which conductors enter shall be closed in an approved manner.

Cheers, Wayne
It uses the word "approved". certainly the entity in charge of such approvals could accept the idea of the floor closing the opening.
 
Status
Not open for further replies.