wiring assistance for low voltage thermostat for electric 240v heater

Status
Not open for further replies.

Saleencook

Member
Location
Louisville, KY
I have a profusion electric 240v heater and would like to wire in an external low voltage thermostat. I have the Aube RC840T-240 relay and not sure where to wire it in the circuit. Profusion manual only shows how to tie in a line voltage thermostat but not a low voltage thermostat.

So not sure if I need to bypass built in thermostat (unwire and cap off) or tie into existing thermostat but turn it up to high.

I’ve attached pics/wiring diagram of circuit.

If someone could draw / show me schematic of new wiring be easier to understand I believe then trying to write it would be of much help
 

Attachments

  • 5BFE58C2-9039-43DF-96B6-666A569D60BC.jpg
    5BFE58C2-9039-43DF-96B6-666A569D60BC.jpg
    7.9 KB · Views: 4
  • 4F67905C-3B16-4DE4-8134-67FABC9AD5FC.jpg
    4F67905C-3B16-4DE4-8134-67FABC9AD5FC.jpg
    8.4 KB · Views: 2
  • 2590E459-8590-4444-AECA-EDE36DA67147.jpg
    2590E459-8590-4444-AECA-EDE36DA67147.jpg
    13.5 KB · Views: 2
Not sure these pics are any better

Not sure these pics are any better

Not sure these pics are any better but really would like some assistance if I can email someone to help out much appreciative
I have a profusion electric 240v heater and would like to wire in an external low voltage thermostat. I have the Aube RC840T-240 relay and not sure where to wire it in the circuit. Profusion manual only shows how to tie in a line voltage thermostat but not a low voltage thermostat.

So not sure if I need to bypass built in thermostat (unwire and cap off) or tie into existing thermostat but turn it up to high.

I’ve attached pics/wiring diagram of circuit.

If someone could draw / show me schematic of new wiring be easier to understand I believe then trying to write it would be of much help
 

Attachments

  • D7948472-5F33-4161-B802-2B8230BE3709.jpg
    D7948472-5F33-4161-B802-2B8230BE3709.jpg
    22.6 KB · Views: 2
  • 4D721A00-C05C-4425-8A9B-1A0431568129.jpg
    4D721A00-C05C-4425-8A9B-1A0431568129.jpg
    15.9 KB · Views: 2
I have a profusion electric 240v heater and would like to wire in an external low voltage thermostat. I have the Aube RC840T-240 relay and not sure where to wire it in the circuit. Profusion manual only shows how to tie in a line voltage thermostat but not a low voltage thermostat.

So not sure if I need to bypass built in thermostat (unwire and cap off) or tie into existing thermostat but turn it up to high.

I’ve attached pics/wiring diagram of circuit.

If someone could draw / show me schematic of new wiring be easier to understand I believe then trying to write it would be of much help
Wire the low voltage stat to terminals R and W on the Aube unit
 
Does that Aube relay have the capacity for the heater you are using? Those are only good for 22 a , I think they make a bigger one.
 