I have a 520a load and I wanted to calculate wire size by tray and by conduit ithink I am correct please confirm
Either case this is a continuos load so 520 x 1.25= 650a cable required
for conduit paralleled conductors i determined 2x700kcm thhn =1040a based on 650a needed
I multiplied 1040a x .82 temp correction 114degrees=852.8
then 852.8 x .80 for 6 current carrying conductors in raceway= 682.24 which is good for 650A ????
In cable tray still 650A required
used 2-500kcm thhn cables with their free air rating 2*700=1400A
Per 3392.80 A(2)b derated by.65 1400 x .65=910
for temp 114 degrees derated by.82 =746????
I believe I am correct could someone please confirm or correct me
Thanks