Re: Wiring for A/C and Heat Pumps
Hi Sparkmantoo, The reason to go with the 40 amp breaker is not for the running load current, it is for the startup current of the motor loads. 2002 NEC 440.22(A) and (B)
Refrigeration compressors take a large amount of current to get them moving.
If you look at 2002 NEC 240.4(G) you will see a list of items that overcurrent protection is treated differently for.
Items in 430 Motors and 440 Air Conditioning and Refrigeration, have much different rules for conductor and short circuit protection.
In a typical lighting circuit the breaker at the panel provides both
overcurrent and short circuit, ground fault protection.
For article 430 and 440 loads the breaker at the panel provides
only short circuit, ground fault protection (phase to phase or phase to ground)
The overcurrent protection of the conductors is provided by the motor overloads that are in the equipment or that you install. Look at 2002 NEC 440.52(B)
There are instances you could have a much larger OCPD at the panel than the conductors are rated for, and still be code compliant.
The key for HVAC loads is to follow the name plate on the unit, I may have been wrong to say you could not use the 30 amp breaker, as the unit said maximum breaker 40, so anything less then that would be code compliant but it may not handle the start up loads.
Where I work we would use the size OCPD they say but we may run larger wire than needed by code for voltage drop reasons.
(Edit in bold, due to wrong info given)
As a side note if the unit tag
only shows fuses, you must have fuses in the circuit.
Here is a link about this.
Topic: fusible disconnects
[ April 18, 2003, 05:47 PM: Message edited by: iwire ]