Hi Folks,
Installing the wiring for a Carier air handler.
Apparently the recommended is 220 15 amp.
Proper breaker to use is a 15amp 2 pole breaker?
Also, HVAC tech, asked for a disconnect to be mounter on unit.
This would be a double pole single throw 15amp switch?
Last question.
Tech asked for an outlet and a 4 square for the low voltage transformer to be mounted on the air handler. The outlet I'm assuming is for the condensate pump.
1. Is it ok to run use the same circuit which is powering the air handler for these. I know i will need to run a 14/3 in order to have a neutral for the 120 volt req of the low voltage transformer and the outlet. Just wasn't sure if it ws ok to use for both.
Thanks in advance.
frank
Installing the wiring for a Carier air handler.
Apparently the recommended is 220 15 amp.
Proper breaker to use is a 15amp 2 pole breaker?
Also, HVAC tech, asked for a disconnect to be mounter on unit.
This would be a double pole single throw 15amp switch?
Last question.
Tech asked for an outlet and a 4 square for the low voltage transformer to be mounted on the air handler. The outlet I'm assuming is for the condensate pump.
1. Is it ok to run use the same circuit which is powering the air handler for these. I know i will need to run a 14/3 in order to have a neutral for the 120 volt req of the low voltage transformer and the outlet. Just wasn't sure if it ws ok to use for both.
Thanks in advance.
frank