positive
Member
- Location
- New Jersey
We have some confustion about an elevator we plan on wiring. We have a single elevator with a nameplate amperage of 121 amps, 3 phase, 208 volt. Our foreman feels that this needs to be wired at 125%. I feel that since we are dealing with an intermittent usage motor, it only needs to be calculated at 85%.
So my calcuations are:
At 121 amps, at 85% = approx. 103 apms. I would size the wire at #3 copper THHN with a 110 amp breaker at main panel with a 110 amp shunt trip breaker in the elevator room.
Please advise me if this is correct. If not, please point me to the correct answer. You can e-mail me at this address:
Poselec@hotmail.com
Thank you,
Mike Gingerelli
Positive Electric Co.
So my calcuations are:
At 121 amps, at 85% = approx. 103 apms. I would size the wire at #3 copper THHN with a 110 amp breaker at main panel with a 110 amp shunt trip breaker in the elevator room.
Please advise me if this is correct. If not, please point me to the correct answer. You can e-mail me at this address:
Poselec@hotmail.com
Thank you,
Mike Gingerelli
Positive Electric Co.