We do many jobs where we add emergency generators for lighting and other purposes to commercial high rise buildings. We just had a seminar where the person running it stated that NEC 2008 700.9(D) states that all wiring that may be routed via a hung ceiling must be fire rated since the feeder-circuit wiring is not installed in an area that is fully protected by the sprinkler system. Is this correct? Sounds pretty insane, especially since there are no such requirements for a 517 hospital emergency system.
 
The requirement is specific to large assembly occupancies and/or 75+ foot (highrise buildings) structures containing specific occupancy types. These structures and occupancies are of "special" concern to life safety during an emergency event due to the large number of people involved or the logistics of getting the people out (egress), thus the fire protection requirement.

(D) Fire Protection. Emergency systems shall meet the additional requirements in (D)(1) through (D)(3) in assembly occupancies for not less than 1000 persons or in buildings above 23 m (75 ft) in height with any of the following occupancy classes: assembly, educational, residential, detention
and correctional, business, and mercantile.

Informational Note: For the definition of Occupancy Classification, see Section 6.1 of NFPA 101-2009, Life Safety Code.

(D)(1) Feeder-Circuit Wiring. Feeder-circuit wiring shall meet one of the following conditions:

(1) Be installed in spaces or areas that are fully protected by an approved automatic fire suppression system

(2) Be a listed electrical circuit protective system with a minimum 2-hour fire rating

Informational Note: UL guide information for electrical circuit protective systems (FHIT) contains information on proper installation requirements to maintain the fire rating.

(3) Be protected by a listed thermal barrier system for electrical system components with a minimum 2-hour fire rating

(4) Be protected by a listed fire-rated assembly that has a minimum fire rating of 2 hours and contains only emergency wiring circuits.

(5) Be encased in a minimum of 50 mm (2 in.) of concrete

(D)(2) Feeder-Circuit Equipment. Equipment for feeder circuits (including transfer switches, transformers, and panelboards) shall be located either in spaces fully protected by approved automatic fire suppression systems (including sprinklerssprinklers, carbon dioxide systems) or in spaces with a 2-hour fire resistance rating.

(D)(3) Generator Control Wiring. Control conductors installed between the transfer equipment and the emergency generator shall be kept entirely independent of all other wiring and shall meet the conditions of 700.10(D)(1).
 
So why would there be a requirement for a highrise office building but not a highrise hospital?
 
Anyway, to get back on point:

I'm working on a fully sprinklered building and now I need to have my cable fire rated because I'm running my feeders above hung ceilings? Is this correct?
 