(D) Fire Protection. Emergency systems shall meet the additional requirements in (D)(1) through (D)(3) in assembly occupancies for not less than 1000 persons or in buildings above 23 m (75 ft) in height with any of the following occupancy classes: assembly, educational, residential, detention
and correctional, business, and mercantile.
Informational Note: For the definition of Occupancy Classification, see Section 6.1 of NFPA 101-2009, Life Safety Code.
(D)(1) Feeder-Circuit Wiring. Feeder-circuit wiring shall meet one of the following conditions:
(1) Be installed in spaces or areas that are fully protected by an approved automatic fire suppression system
(2) Be a listed electrical circuit protective system with a minimum 2-hour fire rating
Informational Note: UL guide information for electrical circuit protective systems (FHIT) contains information on proper installation requirements to maintain the fire rating.
(3) Be protected by a listed thermal barrier system for electrical system components with a minimum 2-hour fire rating
(4) Be protected by a listed fire-rated assembly that has a minimum fire rating of 2 hours and contains only emergency wiring circuits.
(5) Be encased in a minimum of 50 mm (2 in.) of concrete
(D)(2) Feeder-Circuit Equipment. Equipment for feeder circuits (including transfer switches, transformers, and panelboards) shall be located either in spaces fully protected by approved automatic fire suppression systems (including sprinklerssprinklers, carbon dioxide systems) or in spaces with a 2-hour fire resistance rating.
(D)(3) Generator Control Wiring. Control conductors installed between the transfer equipment and the emergency generator shall be kept entirely independent of all other wiring and shall meet the conditions of 700.10(D)(1).